Originally Posted By: Donald
Originally Posted By: Astro_Guy
What is the LRA (Locked Rotor Amperage) rating on the nameplate of the heat pump you want to run? This is the momentary inrush current needed to start the compressor. The RLA (Running Load Amperage) should also be listed on the nameplate, and it will be a small fraction of the LRA. Don't be surprised if the LRA exceeds the capacity of the breaker that protects the unit because we are talking about a momentary load.
When starting an inductive load, such as the compressor on a heat pump, the voltage will drop momentarily which results in more amperage at the same level of power output from your generator. I've read that covering 70% of your LRA load is considered acceptable for commercial applications, and that homeowners might be able to push that figure closer to 50%.
The bottom line here is that you are going to need to perform a load calculation, and that inductive loads like heat pumps cannot be treated the same way as resistive loads like a water heater or electric range. Installing a large, stationary generator is not normally a DIY project, so have some pros help you with this.
I understand the load concerns of starting an electric motor. But my real concern is when the electric booster coils kick in. It's all integrated and I am not sure there is any control of when it kicks in the booster coils.
Sure there is. The heater strips will be wired on their own breaker. Turn it off