What? The lowest nuclear capacity got in Texas was 75% (down 1 unit), and that was due to a sensor line freezing, causing the sensor to trip, because the lines are outside. There were no coolant issues. They unit was brought back as fast as it could be.
Ummm, no, they weren't. A significant portion of the wind turbines were shutdown because they lacked the cold weather package, but even if they had been properly equipped, the situation was similar to Alberta where a cold front such as this rolls in and it brings with it cold, still air, so there isn't much wind to harvest. ERCOT was expecting this, that's why their Winter reliability assessment assumes very low output from wind (they had, at the time, like 28,000MW of installed wind capacity):
View attachment 198620
And here's how it performed:
View attachment 198621
So, for wind:
- Installed capacity was 28,755MW, anticipated output was 7,070MW. Average output was 3,153MW, minimum output hit was 649MW, 2.2% of nameplate.
For solar:
- Installed capacity was 4,898MW, anticipated output was 304MW. Average output was 805MW, minimum output was 0MW.
But would be of no help during this situation, particularly if you were expecting to heat with resistance heating.