Any air conditioning experts in this forum ?

Status
Not open for further replies.
Joined
Dec 20, 2003
Messages
556
Location
Melbourne Australia
Does anyone here know anything about home air conditioning ? I thought I'd throw this thread in here, as I've seen many people here answer tougher off topic questions
smile.gif


We have an add on cooling unit to our central heating. It's a Pioneer, 3 phase, 19kw unit. The house is approx. 32 squares. The heating and cooling is zoned separtely upstairs and downstairs. There is a return air vent both upstairs and downstairs. The whole system, and house, are only 3 years old. The thermostat is a Brivis Networker.

The problem is, the larger of the two copper refrigerant pipes from the indoor coils to the outdoor unit that is covered with foam insulation(I think it's the suction line) becomes frozen because the refrigerant is being forced back to the outdoor compressor. When this happens, the copper pipe freezes up like a balloon, and the indoor temperature keeps rising. The whole air conditioner stops cooling, even though the fans and compressor keep running, and the whole system just wastes electricity.

If the air conditioner has not been used much (ie, if there haven't been many hot days during summer), it fires up and works perfectly. However, the pipe seems to freeze whenever it's been working hard during the day, and there's a drop in outdoor temperature (such as a cool change, common in Melbourne during the summer). The outside temperature will drop, inside temperature in the house will rise from about 23 degrees C to 25 or even 26 degrees C. The compressor will continue to work all night, with the pipe frozen, and the temperature will not drop unless it's significantly colder outside (yeah, I know this wastes money, but it's uncomfortably hot to sleep at night).

Furthermore, if the unit has been working all night with the pipe frozen, and hot weather has been forecast for the remaining few days, the a/c will continue to struggle, and the pipe will remain frozen (I guess because the unit hasn't been off long enough for the refrigerant to unfreeze).

Now for the interesting part - the a/c company who installed the system cheated on us and installed non-genuine Pioneer coils in the roof, without our knowledge or permission
rolleyes.gif
. We only found out when another a/c repair company inspected the coils in the roof. And of course, that same a/c company has gone bankrupt (I wonder why), no longer exist, and of course we now have no warranty.

Some other information -

- The first repairman was an incompetent moron, who reversed the polarity on the compressor, and over-filled the unit with freon, so the compressor would pop and bang when switched on, and not run at all.

- The second repair company, sent by the builder, fixed the above, and drained and re-filled the unit again with freon. But ever since he did this, the pipe has been freezing even worse, and the cooling problems became worse. The cooling capacity was always suspect, and the pipe would always freeze to some extent, but not as badly as it has done last summer and this summer.

- The second repairman fitted a thermostatic expansion valve (TXV) near the compressor on the outdoor unit. We both thought this would fix the problem, but when he hooked up his guages to the unit, it still did weird things, like working perfectly for 5 minutes, before sending refigerant back to the compressor again, and freezing the pipe, and then unfreezing and working perfectly again after a few more minutes.

I have been reading the following website to try and diagnose the problem, but my knowledge of a/c units is limited :
http://www.longviewweb.com/coolfix.htm

In summary, considering all of the above, I can only conclude :

a) The unit is overcharged with refrigerant. Perhaps both repairmen are incompetent, and are not sure what the correct amount of refrigerant the unit requires.

b) There are not enough return air grills in the house for the unit. Less likely, imo, as the unit cools adequately unless the pipe is frozen, as described above.

c) The non-genuine indoor coils are incompatible with the Pioneer outside unit.

d) The whole compressor and outdoor unit are screwed, and need to be taken out the ocean and attached to a anchor and chain
rolleyes.gif
mad.gif


Any advice would be appreciated - hopefully there are some people in this forum who know something about home a/c. Sorry for the long post !
smile.gif
 
Losiho,
I've been repositioning the swamp coolers, adn running around the house trying to work out which windows the breezes are coming through.

Haven't done too bad, as the inside temperature is 32C (better half had an "open windows" policy that resulted in 37.

Not much of a refrigerant bloke...but.

Was commissioning a CO2 plant a while ago.

It had multiple heat exchangers in series, with 8 paralell passes per exchanger...vertical rise of about 4m, then vertical drops, rises etc.

When commissioning the thing, it worked great.

The frost layer rose up the finned tube evenly, then the first tube topped out, and ran down the tube...started a siphon, and destroyed the pressure drop across the evaporator.

All of a sudden, one tube would turn into an ice ball, and the remaining 15 would become blanketted, and lose their ice.

We split the evaporators into a 2 tube 4 pass system, and made everything in series.

So...

I'd check in each circuit how many heat exchangers are in parallel, and what sort of control valves are installed prior to them.

Your statement that it works really well early, but if used for too long short circuits makes me think that one of the parallel paths is either freezing, or able to otherwise create a short circuit.
 
quote:

Originally posted by Shannow:
Losiho,
I've been repositioning the swamp coolers, adn running around the house trying to work out which windows the breezes are coming through.

Haven't done too bad, as the inside temperature is 32C (better half had an "open windows" policy that resulted in 37.

Not much of a refrigerant bloke...but.

Was commissioning a CO2 plant a while ago.

It had multiple heat exchangers in series, with 16 passes per exchanger...vertical rise of about 4m, then vertical drops, rises etc.

When commissioning the thing, it worked great.

The frost layer rose up the finned tube evenly, then the first tube topped out, and ran down the tube...started a siphon, and destroyed the pressure drop across the evaporator.

All of a sudden, one tube would turn into an ice ball, and the remaining 15 would become blanketted, and lose their ice.

We split the evaporators into a 2 tube 4 pass system, and made everything in series.

So...

I'd check in each circuit how many heat exchangers are in parallel, and what sort of control valves are installed prior to them.

Your statement that it works really well early, but if used for too long short circuits makes me think that one of the parallel paths is either freezing, or able to otherwise create a short circuit.


Thanks Steve, I appreciate it.
 
actually, (and yes, I worked for an air conditioning manufacturer for a year or so as an engineer) a frozen suction line (the larger one) is a sign of a couple of things.

For one reason or another, expansion (ie, cooling) is still happening in the return line, past where it should in the inside coil. this can be caused by several things, the most common is a blocked inside (evap) coil. Dust, dirt, pet hair, etc can plug up the airflow across the coil quite easily, even when a filter is used. A good cleaning will fix it up.

The freon is not able to absorb enough heat to fully evaporate witin the coil, so it does some more evaporating (cooling) after the coil, in the suction line. The suction line has no air moving across it to warm it, so it freezes.

Too much freon can also cause this but this is rare in home units unless someone has been adding some recently.
 
Problem will be the evaporator. That's why it will work for a while and then freeze up. What's happening is that there is not enough air movement going to the evaporator coils to "evaporate" the cold pipes. Check the evaporator, evaporator coils, evaporator coil fins, and your return fan. Your return fan could not be pulling air fast enough over the evaporator. Since you said you had morons work on you AC system, that's the first thing I'd check because with the heat in Austrialia, you should not have freezing pipes.
 
The most likely problem is a plugged filter or dirty evap coils. In any event you are not passing enough air accross the evap coils-indoor unit I can almost guarantee that is the problem. In rare cases the fan could be running at too low rpm (defective fan) Make sure you are getting enough air supply. Also closing too many of the returns or supply could be the problem.

Its possible that the unit is overcharged but very unlikely.

Check the registers, check the filter, check the coils. Also there could be two filters in line. One might be plugged. Filter, filter, filter. Let us know.
 
quote:

Originally posted by Bob Woods:
. Sounds to me like you have low freon.

Low freon will not give freezing temps at the outlet of the indoor unit. You would normally have frost in the first third or so of the indoor unit withlow freon.
 
Thanks for the links guys !
smile.gif


Kenw - Both repairmen went into the ceiling and both said the coils weren't dirty or blocked, but who knows. Could the coils be too small for the system ? And yes, as I mentioned, the system has been filled with freon twice in the last 12 months (both times drained completely before refilling).

Schmoe - Is there any way to adjust the fan speed in the return air line ?

Al - Filters are absolutely clean ! There is no restriction there. Could there be not enough / too small return air vents, as I mentioned ?
 
quote:

Originally posted by Losiho:
Thanks for the links guys !
smile.gif


Kenw - Both repairmen went into the ceiling and both said the coils weren't dirty or blocked, but who knows. Could the coils be too small for the system ? And yes, as I mentioned, the system has been filled with freon twice in the last 12 months (both times drained completely before refilling).

Schmoe - Is there any way to adjust the fan speed in the return air line ?


You usually change fan speeds by selecting different terminals in the fan housing. Is there a bypass around the coils. It is possible that you have one big block of Ice closing off your coils. Are you getting good flow out of your suppply registers. Like I said there might be a filter somewhere else. You need to physically look at the coils. You are not taking heat away from those indoor coils. So its

1. Plugged filter
2. Dirty Coils
3. Iced up coils
4. Inadequate fan supply

Feel if you are getting good air flow out registers..I'll bet you aren't.

Let the fan run constantly-without A/C on if you can't inspect the coils. This will melt the Ice. Usually there is an inspection plate you can remove to look at coils. Its possible a filter or something let loose and is blocking the coils. U are just not gettting the flow. Oh also turn Off the humidifier if there is one.
 
The temp and pressure of freon are directly related to each other. The ideal system allows the low side to operate at a temp just above freezeing. If the freon is low the temp drops below freezeing and even the evap coil will turn into a block of ice. Sounds to me like you have low freon.
 
Techs were back again today.

I showed them a copy of the Pioneer a/c installation sheet I had lying around from when the unit was purchased. Seems that the liquid line is smaller than it needs to be. Spec sheet says half a inch, the line running to the ceiling is smaller. The installers welded a smaller liquid line to the half inch pipe inside the a/c condensor unit.

They will come back next week and replace the liquid line and fit a TXV next to the condensor unit.
 
when our ac was installed, it took a couple of times for the guys to 1) use the correct solder and 2) sweat the pipe right.

we initially had some solder inside the line, and it would plug rather quickly once things were going.
 