Recent Topics
A01s From Korea branded FourGreen?
by David1. 07/17/19 05:01 AM
New pennzoil rebate 7/16-12/31/19
by pdxglocker9mm. 07/17/19 03:11 AM
'82 BMW 733i M30 - Which Oil
by TXCarGeek. 07/17/19 02:07 AM
Aother MEGA score+Free Mobil 1 oil change
by GMguy84. 07/17/19 12:39 AM
I think I need therapy...
by tony1679. 07/16/19 11:53 PM
Hellcat engine in a Miata
by hate2work. 07/16/19 09:59 PM
Alignment shop questions
by Jeff999. 07/16/19 09:45 PM
ZF Aftermarket, Why Change Your ATF
by BMWTurboDzl. 07/16/19 08:10 PM
Goodyear Wrangler DuraTrac
by NHRATA. 07/16/19 08:05 PM
5 qt Castrol GTX Magnatec 5w-30 $10.30 on Amazon
by gallydif. 07/16/19 07:59 PM
My new rig - 1987 Ford Econoline 27' Glendale RV
by caprice_2nv. 07/16/19 07:44 PM
Air Compressor OCI?
by Vern_in_IL. 07/16/19 07:35 PM
Looking for an SUV
by dgunay. 07/16/19 07:29 PM
Castrol GTX Magnatec 5w30
by Envoyguy. 07/16/19 07:21 PM
2019 Subaru Dual X-Mode
by buster. 07/16/19 06:36 PM
Wear Metal Max?
by tsm750. 07/16/19 05:54 PM
Harbor Freight 25% off Thurs - Sunday
by JC1. 07/16/19 05:52 PM
80% Furnace exhaust silencer?
by PandaBear. 07/16/19 05:10 PM
Pennzoil Ultra on Sale
by Nyati. 07/16/19 04:39 PM
Not All Mid-Grade Blended At the Pump
by RayCJ. 07/16/19 04:30 PM
Newest Members
MBhuntington, captainfloss, Lyndol, Belczek, Bronco628
68681 Registered Users
Who's Online Now
51 registered members (Bailes1992, cjcride, bbhero, Char Baby, cristo, 5 invisible), 742 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Forum Statistics
Forums67
Topics291,974
Posts5,014,322
Members68,681
Most Online2,967
Mar 10th, 2019
Donate to BITOG
Hop To
Page 4 of 4 1 2 3 4
Re: GFCI weirdness [Re: researcher] #4784685
06/12/18 09:05 AM
06/12/18 09:05 AM
Joined: May 2004
Posts: 10,597
Nokesville, VA
brianl703 Offline
brianl703  Offline

Joined: May 2004
Posts: 10,597
Nokesville, VA
Originally Posted By: researcher
now let me ask this.. would the "problems" that GFCI have also be applied to AFCI outlets?


Yes, in that a poorly-designed AFCI can trip when it should not, just as a poorly-designed GFCI will.

Yes, in that an AFCI contains electronic circuitry that can degrade/fail over time, just as a GFCI does.

Re: GFCI weirdness [Re: brianl703] #4784732
06/12/18 09:57 AM
06/12/18 09:57 AM
Joined: Oct 2009
Posts: 75
ca
westom Offline
westom  Offline

Joined: Oct 2009
Posts: 75
ca
Originally Posted By: brianl703

Yes, in that a poorly-designed AFCI can trip when it should not, just as a poorly-designed GFCI will.

How does an RF transmitter cause a trip? Correlation never creates a fact. He assumed the transmitter will always cause a problem. IOW he saw a symptom. Then used speculation to conclude it is acceptable.

GFCIs are routinely found in transmitter stations where radiated power is massive. GFCIs do not trip. Yes, it is possible that electronics inside one GFCI were defective - a manufacturing defect. Everyone has seen them. Even counterfeit electrolyte in capacitors caused electronics to fail many years later. Another manufacturing defect that we all know about. That does not say GFCIs are defective.

Electronics should work for many decades without failure. Manufacturing defects can exist. But GFCIs rarely fail. That GFCI apparently was reporting a defective sump pump. So he removed the GFCI - killed the messenger - to deny a human safety threat exists.

Always first identify and then fix a defect. If a transmitter might cause a GFCI to trip, then the reason why is learned. Never once saw a portable transmitter adjacent to a GFCI trip that GFCI (or AFCI). Never cure symptoms. GFCI is not defective - a pump apparently is.

Re: GFCI weirdness [Re: JHZR2] #4784906
06/12/18 01:43 PM
06/12/18 01:43 PM
Joined: May 2004
Posts: 10,597
Nokesville, VA
brianl703 Offline
brianl703  Offline

Joined: May 2004
Posts: 10,597
Nokesville, VA
As I stated previously: GFCIs are required for sump pump outlets not because a sump pump ground fault might exist, but because someone may use that outlet as a general-use receptacle.

A hard-wired sump pump is not required to be on a GFCI. Only a cord-and-plug connected sump pump.

His pump maybe defective. Mine definitely isn't.

Electronics do not work for many decades without failure UNLESS designed that way---and that increases cost. Any use of electrolytic capacitors, for example, dooms the circuit to an eventual failure when, not if, but when the rubber seal on that capacitor fails.

On GFCI failure rate, if I had to choose between "never, rarely, sometimes, often, always" I would say that they "sometimes" fail.

In my experience, as the age of the GFCI approaches 10 years, the failure rate is about 100%. This is for GFCIs of a particular brand produced in the mid 90s. Newer production GFCIs may be more reliable--GFCIs produced in the mid-00s of the same brand have not needed replacement yet.

Re: GFCI weirdness [Re: JHZR2] #4784908
06/12/18 01:47 PM
06/12/18 01:47 PM
Joined: May 2004
Posts: 10,597
Nokesville, VA
brianl703 Offline
brianl703  Offline

Joined: May 2004
Posts: 10,597
Nokesville, VA
An interesting read on what conditions can cause nuisance tripping:

http://www.ecmweb.com/content/think-gfci

Re: GFCI weirdness [Re: westom] #4784911
06/12/18 01:49 PM
06/12/18 01:49 PM
Joined: Nov 2008
Posts: 13,958
NH
supton Offline
supton  Offline

Joined: Nov 2008
Posts: 13,958
NH
Originally Posted By: westom
GFCIs are routinely found in transmitter stations where radiated power is massive. GFCIs do not trip.


I'd have to think transmitter stations have more power line filtering and probably ran the wiring inside of conduit. Thus lowering picked up RF. All wiring inside of a metal box with good shielding and ground practices vs typical house with none.


2011 Toyota Camry, base, 2.5L/6MT, 187k, hers
2010 Toyota Tundra DC, 4.6L/6AT, 152k, ours
1999 Toyota Camry LE, 2.2L/4AT, 208k, his
Re: GFCI weirdness [Re: brianl703] #4785114
06/12/18 05:48 PM
06/12/18 05:48 PM
Joined: Oct 2009
Posts: 75
ca
westom Offline
westom  Offline

Joined: Oct 2009
Posts: 75
ca
Originally Posted By: brianl703
An interesting read on what conditions can cause nuisance tripping.

Unfortunately it does not say anything about why. It is a subjective warning about what may and may not work. And that, unfortunately, is vague, subjective reasoning that does not say why with numbers.

Those GFCI testers can only report some defects; can never say anything is good.

A sump pump can be leaking 4 milliamps constantly - and not trip a GFCI. One connects another appliance which causes a GFCI trip. Subjective reasoning (also called junk science) then blames the other appliance.

Meanwhile I built a tester than intentionally created an adjustable leakage current. So that I can measure how much leakage causes a GFCI to trip. Good GFCI trips at between 4 to 6 milliamps. If it trips lower, then we know some other appliance has a human safety threat. So it may cause 'nuisance tripping'.

All honest discussions define everything quantitatively. That means numbers are always included. No numbers is a first indication that it might be a scam.

Second, a transmitter should not create a 5 milliamp current on AC wires. GFCIs work just fine in the massive E-M fields even in transmitter facilities. However it can induce micro-amp currents. That combined with leakage elsewhere could result in 'nuisance tripping'. Solution- find and fix that unacceptable other leakage. Never foolishly make a conclusion from myths that blame 'nuisance tripping'.

One always learns what is defective long before making accusations or a conclusion. Classic junk science is to see a GFCI trip. Then wildly speculate it was caused by some other (perfectly safe) appliance or a radio transmitter.

That sump pump apparently has a human safety defect. So someone with contempt for human life used a classic urban myth (nuisance tripping) to justify removing a GFCI. Used a conclusion only from wild speculation to endanger human life.

Long before making such conclusions, the informed first learn the whys with numbers. One who cannot must find someone to teach or somehow to learn basic electrical concepts before making a conclusion. 'Nuisance tripping' is an 'easy to promote' urban myth.

Re: GFCI weirdness [Re: westom] #4785662
06/13/18 09:17 AM
06/13/18 09:17 AM
Joined: May 2004
Posts: 10,597
Nokesville, VA
brianl703 Offline
brianl703  Offline

Joined: May 2004
Posts: 10,597
Nokesville, VA
Originally Posted By: westom


A sump pump can be leaking 4 milliamps constantly - and not trip a GFCI. One connects another appliance which causes a GFCI trip. Subjective reasoning (also called junk science) then blames the other appliance.


Any GFCI installed for a sump pump is to be on a dedicated circuit for use of the sump pump ONLY. This is code. Plugging another appliance into GFCI outlet dedicated for a sump pump is misusing the outlet, and is not permitted in any facility under my control.

Re: GFCI weirdness [Re: brianl703] #4786168
06/13/18 07:30 PM
06/13/18 07:30 PM
Joined: Oct 2009
Posts: 75
ca
westom Offline
westom  Offline

Joined: Oct 2009
Posts: 75
ca
Originally Posted By: brianl703
Any GFCI installed for a sump pump is to be on a dedicated circuit for use of the sump pump ONLY.

So you completely missed the points. Again:

A pump leaking four milliamps can create 'nuisance tripping'. It may trip that GFCI every day. Or it may trip it once after many weeks or once every six or twelve months. That 'nuisance trip' is reporting a defect.

Even the microamp current from a nearby transmitter could have that 'nuisance trip' ... that is actually reporting a potential human safety threat.

Second, conclusions only from observation are classic junk science. If the GFCI it tripping, then one finds a defect long before making any conclusion. 'Nuisance tripping' (as demonstrated by some contributors here) is typical of conclusions only from observation.

And third, I have never seen the National Electrical code require a sump pump on a dedicated circuit. Apparently that is either a local code or a workmanship standard. A good habit. But not required.

Last edited by westom; 06/13/18 07:31 PM.
Re: GFCI weirdness [Re: JHZR2] #4786259
06/13/18 09:30 PM
06/13/18 09:30 PM
Joined: Sep 2015
Posts: 1,936
USA
mk378 Offline
mk378  Offline

Joined: Sep 2015
Posts: 1,936
USA
An AFCI detects high frequency currents to the load. There are some loads which do that "normally" and can cause unnecessary tripping of the AFCI. This is different from a GFCI. Ground faults are never normal.

Last edited by mk378; 06/13/18 09:32 PM.
Re: GFCI weirdness [Re: mk378] #4803223
07/02/18 02:04 PM
07/02/18 02:04 PM
Joined: Oct 2009
Posts: 75
ca
westom Offline
westom  Offline

Joined: Oct 2009
Posts: 75
ca
Originally Posted By: mk378
There are some loads which do that "normally" and can cause unnecessary tripping of the AFCI.

A responsible post because it also says why. Some defices can create that high frequency noise. And then we found the defect that made that possible. For example, electronics that drove a paper shredder would trip that breaker.

We opened it. Clearly marked on its PC board were holes for the required line filter. We see this often. An engineer designed what is necessary. Then a business school graduate uses his cost control mentality to cut costs. Apparently that business school graduate discovered a shredder worked just fine without that line filter. So the filter was replaced with jumper wires. To increase profits.

I obtained and installed an exact same filter from an old TV. It even matched all holes. Then a breaker stopped tripping.

Don't blame the AFCI breaker. Blame the defective appliance that creates noise - that even FCC regulations say must not exist. What is the most common reason for such failures? Bosses who have no idea how the work gets done.