Recent Topics
Very Basic Engine Question
by Ducked
04/21/18 11:16 PM
K&N Air Filter for FJ
by CCI
04/21/18 10:41 PM
Shoutout of the day... Thanks car51!
by SubieRubyRoo
04/21/18 10:15 PM
PTFE rear main seal installed NOT dry
by eyeofthetiger
04/21/18 09:22 PM
Why call standard spark plugs “copper plugs”?
by y_p_w
04/21/18 08:58 PM
Sesame seed oil for chicken marinade?
by aquariuscsm
04/21/18 08:39 PM
Microgreen M G 201-7 6k, CUT OPEN
by car51
04/21/18 08:34 PM
NAPA PLATINUM 41516, 17.2k CUT OPEN
by car51
04/21/18 08:24 PM
They don't make 'em like they used to...
by Alex_V
04/21/18 06:55 PM
5W-20 P.U.P. at Walmart (yes, in stock!) $24.97
by Linctex
04/21/18 06:37 PM
Havoline ProDS 10w30 on Rollback at Walmart
by JohnnyJohnson
04/21/18 05:43 PM
Richmond Raceway
by Warstud
04/21/18 05:40 PM
2009 Mustang GT
by GMFan
04/21/18 05:22 PM
Is your A/C ready for the summer?
by Nick1994
04/21/18 04:51 PM
Pennzoil Synthetic Rollback Walmart
by FordBroncoVWJeta
04/21/18 04:48 PM
Alternators, A just in case Scenario.
by rollinpete
04/21/18 04:38 PM
Palm Ratchets
by 2015_PSD
04/21/18 04:32 PM
2013 Equinox ATF change
by Dave Sherman
04/21/18 04:13 PM
Champion vs NGK Spark Plugs ?? Iridium
by fins
04/21/18 03:46 PM
Are you driving the same car since 2010
by CourierDriver
04/21/18 03:45 PM
Newest Members
Marc32275Jax, puma4440, zeroyon223, wade12345, rdatman
64806 Registered Users
Who's Online
48 registered (bdcardinal, BAJA_05, andyd, antonmnster, 69Torino, 3 invisible), 983 Guests and 34 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
64806 Members
68 Forums
282100 Topics
4709884 Posts

Max Online: 3590 @ 01/24/17 08:07 PM
Donate to BITOG
Page 1 of 2 1 2 >
Topic Options
#4697762 - 03/17/18 04:59 PM “Back feeding” generator to breaker box
Finz Offline


Registered: 06/06/13
Posts: 677
Loc: Northern NJ
I know this isn’t to code and can be dangerous but I believe my approach will work safely until I’m ready for a more permanent system

I have 150 amp service into a Cutler Hammer box with 2 hot busbars running parallel from top to bottom

I’ve added a 20 amp breaker to the each of the busbars using 10 gauge

Each of these are being fed into a 2 pole 30 amp service interrupt

From the service interrupt, I’ll run 10 gauge out thru the wall to a 4 prong outlet

I have a powermate 7,500/6,000 watt generator and will use a 30’ power cord

I’ve been doing this with loose wire since Sandy but I simply fastened the wires direct to the busbars. The above will backfeed in the same way but save me the trouble of attaching the wires

I always shut main service off and all breakers. Attach the wires, start the generator and then, very selectively, turn on breakers as needed: Kitchen lights, WiFi, .... we draw very little at any one time.

Gas heat, oven and hot water so, if I need heat, run only the pump on boiler

So my question:

I have 2 runs of 10/2 coming out of the service interrupt. I want to run these to the exterior outlet which will accept a 4 prong

I have 2 commons, 2 grounds and 2 hot.

How do I wire the outlet? Just pigtail as needed?

Thank you for any input
_________________________
God Bless America... We really need it about now

06 Odyssey
06 Civic coupe
05 Accord 2.4 sedan
11 Civic 1.8 sedan
98 Accord 2.3 sedan

Top
#4697770 - 03/17/18 05:12 PM Re: “Back feeding” generator to breaker box [Re: Finz]
Astro_Guy Offline


Registered: 07/30/15
Posts: 397
Loc: Pennsylvania
This seems a little foolish to me, although I will admit that I don't know what you mean by "2 pole 30 amp service interrupt". What you need is a transfer switch wired to specific circuits. There is simply no way that should ever wire your generator directly to the bus bars; to do that you MUST go thru a full service transfer switch rated to at least your your service level.
_________________________
'10 Honda Civic, 102K miles, 0w20 M1 EP
'01 Volvo V70XC, 222K miles, 0w40 M1

Top
#4697773 - 03/17/18 05:19 PM Re: “Back feeding” generator to breaker box [Re: Finz]
Snagglefoot Offline


Registered: 12/31/17
Posts: 1278
Loc: Alberta
“ I know this isn’t code and could be dangerous” = no house insurance. Astro guy is right. The Transfer switch is not that much.

Top
#4697794 - 03/17/18 05:39 PM Re: “Back feeding” generator to breaker box [Re: Astro_Guy]
Finz Offline


Registered: 06/06/13
Posts: 677
Loc: Northern NJ
Originally Posted By: Astro_Guy
This seems a little foolish to me, although I will admit that I don't know what you mean by "2 pole 30 amp service interrupt". What you need is a transfer switch wired to specific circuits. There is simply no way that should ever wire your generator directly to the bus bars; to do that you MUST go thru a full service transfer switch rated to at least your your service level.


I hear you but here’s my thought process:

The 2 pole service interrupt is nothing more than a cut-off with a 30 amp fuse

At no time will I be drawing more than 15 amps (my fridge)

The lights, WiFi and tv are negligible

The largest circuit in the box is 20 amp.... granted a 30 amp 2 pole for AC but I’d never use it

With the generator isolated, my service level is 30 amps. My interrupt is 30 amps. My max usage if 15 amps

Let me try it another way:

A transfer switch is used to provide juice to 4, 6,.... circuits you want juiced. They are run from the same breaker to the switch and, once the switch is turned on, the main is, at the same time, cut off via that plate

What I’m doing is, in lieu of the transfer switch, I have 2 breakers connected to the box, which feed to my interrupt/cutoff

Instead of having 4, 6, ... dedicated breakers, I pick and choose

The only difference, as I see it, is I simply don’t have the safety protocol whereby the the main for transfer automatically cuts off main from service. I have to do it manually

What am I missing

...understood about the homeowners insurance



Edited by Finz (03/17/18 05:40 PM)
_________________________
God Bless America... We really need it about now

06 Odyssey
06 Civic coupe
05 Accord 2.4 sedan
11 Civic 1.8 sedan
98 Accord 2.3 sedan

Top
#4697796 - 03/17/18 05:52 PM Re: “Back feeding” generator to breaker box [Re: Finz]
mk378 Online   content


Registered: 09/27/15
Posts: 1325
Loc: USA
Nobody reputable is going to tell you how to do this. It is extremely dangerous on several fronts if you forget to open the main breaker. A transfer switch is designed to be absolutely fail safe against both operator error and equipment failure.

As someone else noted, you can put a large transfer switch between the electric meter and the main breaker. This gives you the flexibility to energize any circuit, subject of course to not overloading the generator. Overloading the generator is actually the least of your concerns here.


Edited by mk378 (03/17/18 05:55 PM)

Top
#4697808 - 03/17/18 06:04 PM Re: “Back feeding” generator to breaker box [Re: Finz]
mattwithcats Offline


Registered: 06/13/13
Posts: 1613
Loc: Virginia
PBS did an episode of “This Old House” on how to hook up a emergency generator using a transfer switch...

https://youtu.be/GLgtFCJlVFQ

Smaller 6 circuit transfer switch, they used a 10 circuit version in the video...

https://www.homedepot.com/p/Reliance-Controls-30-Amp-6-Circuit-Manual-Transfer-Switch-306A/206499418


Edited by mattwithcats (03/17/18 06:08 PM)
_________________________
2009 Smart Pure
Pennzoil Platinum Euro 0W-40, Purolator Synthetic PSL 14610, 45 mpg...
185/55R15 General HP tires, "H" speed rated, 44 psi (300 kpa)

Top
#4697825 - 03/17/18 06:17 PM Re: “Back feeding” generator to breaker box [Re: Finz]
mrsilv04 Offline


Registered: 12/08/06
Posts: 8145
Loc: Illinois
Burn your house down if you must... .but please don't kill the lineman with the power company, who is working on the pole out by the road.
_________________________
2004 Silverado - on its 3rd Jasper engine in less than one year.

Top
#4697867 - 03/17/18 06:51 PM Re: “Back feeding” generator to breaker box [Re: Finz]
bubbatime Offline


Registered: 03/18/08
Posts: 5456
Loc: South Florida
Buy the $50 kit and do it right? The correct answer is so easy a cave man could come up with it.

And most folks back-feed through the dryer 220 outlet.
_________________________
17 Chrysler Pacifica QS syn 0W20
13 Yamaha XT250 Valv MC 10W40
12 Suzuki S40 Rotella 15W40
10 Acura TSX 2.4 ST syn 5W20
06 GMC Sierra Nextgen 10W30



Top
#4697870 - 03/17/18 06:53 PM Re: “Back feeding” generator to breaker box [Re: mrsilv04]
dschultz Offline


Registered: 01/14/06
Posts: 5
Loc: Virginia
The right way (depending on local code approval) is this:
https://www.interlockkit.com
A breaker interlock kit that installs in your panel so the main will always be off before the breaker from the generator is closed.

This is the only safe way without an external circuit based or service based transfer switch.

I just run extension cords to run what I need. I only have a 120V generator so I can't power 240v Loads anyway.

When I replace my panel I will get one with an interlock kit for transfer.

Be safe!


Edited by dschultz (03/17/18 06:55 PM)
Edit Reason: can't type the first time!

Top
#4697927 - 03/17/18 07:28 PM Re: “Back feeding” generator to breaker box [Re: Finz]
JimPghPA Offline


Registered: 08/22/09
Posts: 3824
Loc: Pittsburgh,PA U.S.A.
To the OP, I found an incoming main/generator transfer switch rated at 200 amps for the main and 50 amps for the generator for $114 on e-bay a couple of years ago. I have not looked at the availability lately but you might check e-bay.
_________________________
Boy will I be happy when ALL vehicles on public roads are autonomous.


JimPghPa


Top
#4697944 - 03/17/18 07:47 PM Re: “Back feeding” generator to breaker box [Re: Finz]
Linctex Offline


Registered: 12/31/16
Posts: 5665
Loc: Waco, TX
Get one of these (Generator Interlock Kit) and be done with it

_________________________
"The evidence demands a verdict".
(Re:VOA)"it's nearly impossible to actually know the particular additives that are in there at what concentrations."

Top
#4697962 - 03/17/18 08:02 PM Re: “Back feeding” generator to breaker box [Re: Finz]
jhellwig Offline


Registered: 07/01/13
Posts: 1414
Loc: Ottumwa, Iowa
No no no no no no no no just no. Do it right or don't do it at all. Don't play around with electricity.
_________________________
Sparks fly from my fingers.

1995 Chevy K2500 Suburban lt 5.7
2008 Chevy Suburban 5.3
1983 Chevy K5 350

Top
#4698020 - 03/17/18 08:57 PM Re: “Back feeding” generator to breaker box [Re: Finz]
walterjay Offline


Registered: 04/12/09
Posts: 203
Loc: Maryland
Absolutely do not backfeed your generator into your electrical system. Much at stake here including the safety of lineman. Get an interlock or transfer switch please. My next door neighbor almost caught his house on fire doing something like you. Generator interlock kits are inexpensive and makes all safe.

Top
#4698072 - 03/17/18 09:38 PM Re: “Back feeding” generator to breaker box [Re: Finz]
Reddy45 Online   shocked


Registered: 08/15/08
Posts: 2725
Loc: USA
If you're going to do this, notify your power company because you could kill one of their workers.

Top
#4698117 - 03/17/18 10:19 PM Re: “Back feeding” generator to breaker box [Re: Reddy45]
Leo99 Offline


Registered: 03/30/14
Posts: 2874
Loc: NJ
Originally Posted By: Reddy45
If you're going to do this, notify your power company because you could kill one of their workers.


That's what I was thinking. You'll power lines from your generator that have the main power shut off to them and endanger the workers.
_________________________
Without data you're just another person with an opinion. W. E. Deming