Recent Topics
Update password ?
by meadows
06/17/18 11:59 PM
Delayed Sleep Phase Disorder
by Reddy45
06/17/18 11:56 PM
Nissan DLR put 0w20 in car that specs 5w30. worry?
by CrAlt
06/17/18 10:40 PM
revive Nicd battery
by Donald
06/17/18 10:27 PM
Need help finding an apartment for friend
by RazorsEdge
06/17/18 10:07 PM
ceratec with redline 5w30?
by 08z06
06/17/18 09:53 PM
does your COMCAST modem have weak wifi??
by edwardh1
06/17/18 09:50 PM
I hate stuck thermostats
by jakewells
06/17/18 09:49 PM
Mag1 75w90
by SavagePatch
06/17/18 09:32 PM
Old batteries at HD
by bbhero
06/17/18 09:27 PM
Buying a CPO Toyota - still get inspected?
by Parlay_Slow
06/17/18 09:08 PM
Water Pump Paper Gasket With RTV? Longevity?
by nobb
06/17/18 08:22 PM
Who makes Briggs & Stratton oil?
by spk2000
06/17/18 08:13 PM
Shure stylus replacement
by aquariuscsm
06/17/18 07:54 PM
Any 'crazy UCL overdose' fans out there?
by addyguy
06/17/18 07:11 PM
Source for Castrol Edge Supercar 5w50 oil?
by Rainier42
06/17/18 06:50 PM
Cherry vs orange hand cleaner
by JHZR2
06/17/18 06:27 PM
Why buy low mileage tires?
by HowAboutThis
06/17/18 05:49 PM
Mercury 35-8M0065104 cut open w/ oil change pics
by dlundblad
06/17/18 05:37 PM
2019 Hondaís miniMOTOs (125cc)
by DuckRyder
06/17/18 05:18 PM
Newest Members
mostdecent, T1TN, Piper58, dunlop0078, Truth_Syrup
65258 Registered Users
Who's Online
31 registered (bubbatime, AVB, bbhero, bdcardinal, Bryanccfshr, askani79705, 5 invisible), 973 Guests and 36 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
65258 Members
67 Forums
285502 Topics
4764666 Posts

Max Online: 3590 @ 01/24/17 08:07 PM
Donate to BITOG
Topic Options
#4687781 - 03/07/18 04:37 PM Generator connection
Donald Offline


Registered: 03/21/04
Posts: 20446
Loc: Upstate NY
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.


Edited by Donald (03/07/18 04:39 PM)
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2016 Subaru Crosstrek CVT (wife's)


Top
#4687806 - 03/07/18 05:02 PM Re: Generator connection [Re: Donald]
WyrTwister Offline


Registered: 01/13/13
Posts: 1487
Loc: Texas
I would change " gender " of the outlet .

Be 100% certain you do not end up with a system where the blades on the male do not end up " hot " when the generator is running .

If they are exposed & flopping around , some one may easily get " bit " .
_________________________
Wyr
God bless

Top
#4687819 - 03/07/18 05:14 PM Re: Generator connection [Re: Donald]
Donald Offline


Registered: 03/21/04
Posts: 20446
Loc: Upstate NY
The outlet has a snap cover so if a connector is not inserted the outlet will be covered.
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2016 Subaru Crosstrek CVT (wife's)


Top
#4687836 - 03/07/18 05:23 PM Re: Generator connection [Re: Donald]
Jim_Truett Offline


Registered: 01/07/09
Posts: 277
Loc: San Diego, California
Sounds like the box has an Inlet, not an Outlet. You will need to change it to be safe and legal.
_________________________
2008 F250 6.4 PowerStroke 43k
2005 Honda CR-V 193k
2005 Honda Pilot 235k
1963 Nova SS 84k
2015 Civic Si 23k
2013 Mahindra 3016HST 99hrs

Top
#4687894 - 03/07/18 06:11 PM Re: Generator connection [Re: Donald]
Linctex Offline


Registered: 12/31/16
Posts: 6148
Loc: Waco, TX
What are your plans for said generator?

Emergency stand-by, or......?
_________________________
"The evidence demands a verdict".
(Re:VOA)"it's nearly impossible to actually know the particular additives that are in there at what concentrations."

Top
#4687943 - 03/07/18 06:55 PM Re: Generator connection [Re: Donald]
Donald Offline


Registered: 03/21/04
Posts: 20446
Loc: Upstate NY
It will be a backup and will power parts of my home via a generator cord.
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2016 Subaru Crosstrek CVT (wife's)


Top
#4687986 - 03/07/18 07:24 PM Re: Generator connection [Re: Donald]
Snagglefoot Online   content


Registered: 12/31/17
Posts: 1680
Loc: Alberta
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.


Sounds like someone wired it so they could run a conventional cord to your generator. Youíre supposed to use a special generator cord. They wired it like an RV trailer but didnít realize itís against code because a house can be powered from the grid but the RV would not.

Top
#4688066 - 03/07/18 08:32 PM Re: Generator connection [Re: Donald]
Snagglefoot Online   content


Registered: 12/31/17
Posts: 1680
Loc: Alberta
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.


Checked it out and assuming your inlet was wired correctly, you have the correct configuration. . My comments above are incorrect. The inlet to the house will be a male plug. This will allow a heavy gauge cord to be plugged into the female plug on the generator and the female end of the generator cord will plug into the house. Inside will be a switch that will isolate the grid from the house and allow the inlet to the house to connect to the house wiring. When wired correctly there is no way for grid power to energize the male plug. Also when done correctly your house breakers willl still be functional. Hope that helps.

Top
#4688517 - 03/08/18 09:29 AM Re: Generator connection [Re: Donald]
Schmoe Offline


Registered: 05/12/03
Posts: 7256
Loc: Oklahoma
That's what I've done, but the opposite. Installed a 50 amp breaker and a dedicated female plug in the garage. Output from the generator to a 50 amp rated cord connected to a male plug that goes into that house female plug. First, turn off the main breaker so there is no back feed. Hook up all the cables and make sure 50 amp house breaker is off AND ALL THE OTHER breakers are off. Fire up generator and let warm up. Turn on breakers from the generator, turn on dedicated 50 amp house breaker, then slowly turn on the home breakers that I need. You'll have to label all your breakers for the house because some of them you won't need to use and save power for the generator. I keep the kitchen one on, stove is a 40 amp breaker and it stays off, living room, bathroom, one bedroom and the floor freezers if it is in summer time, but those things stay insulated for a pretty long time. Yeah, I know it's not the right way to do it and technically illegal, but in a pinch, it will work.
_________________________
01 Supercrew Lariat 4X4
06 Accord EX-L V6
14 CRV EX-L



Top
#4688556 - 03/08/18 10:09 AM Re: Generator connection [Re: Donald]
Snagglefoot Online   content


Registered: 12/31/17
Posts: 1680
Loc: Alberta
The problem with technically illegal is that you technically have no house insurance. Just install the proper isolation switch and breaker. If someone throws the main breaker you can electrocute a lineman.

Top
#4688698 - 03/08/18 12:33 PM Re: Generator connection [Re: Donald]
dnewton3 Offline



Registered: 05/14/07
Posts: 7389
Loc: Indianapolis, IN
I have built my last two homes myself (acted as GC and did a lot of the work myself).

When I wired my homes, I put in a few secondary circuits to the major items (furnace, fridge, septic pump, tv, etc).
Each outlet has a twin circuit; one side for Duke energy and one for the Generator. (if you break the little tab between the sockets, they become independent outlets).

All I have to do is power my secondary distribution box, then pull the appliance cord from the Duke side and into the Gen side. Viola!

And no risk whatsoever of killing a worker upstream by powering the main line into a hot condition.
_________________________
The act of preventative maintenance, in and of itself, is FAR MORE important than brand/grade/base choices among lubes and filters.
- under maintaining something is akin to abuse/neglect; that can kill equipment by shortening the lifespan
- over maintaining something has never been proven to be anything but a waste of time and money

Top
#4688705 - 03/08/18 12:41 PM Re: Generator connection [Re: Donald]
WyrTwister Offline


Registered: 01/13/13
Posts: 1487
Loc: Texas
There are many was of doing it wrong which work either most of the time or all the time . But still , they are unsafe .
_________________________
Wyr
God bless

Top
#4688732 - 03/08/18 01:12 PM Re: Generator connection [Re: Donald]
Whimsey Offline


Registered: 12/22/02
Posts: 4047
Loc: The Garden State
When I bought my 5500 watt B&S portable generator I also got a Reliance manual transfer switch. Mine's a 6 circuit switch. It's set up to not be able to back feed from the generator to the circuit breaker panel. It's either only off, line or generator so it can't back feed. It has a male 30 amp receptacle to plug the female end of the 30 amp cord plugged into the generator.

Whimsey

Top
#4689201 - 03/08/18 09:41 PM Re: Generator connection [Re: Schmoe]
Linctex Offline


Registered: 12/31/16
Posts: 6148
Loc: Waco, TX
Originally Posted By: Schmoe
That's what I've done, but the opposite. Installed a 50 amp breaker and a dedicated female plug in the garage. Output from the generator to a 50 amp rated cord connected to a male plug that goes into that house female plug. First, turn off the main breaker so there is no back feed. Hook up all the cables and make sure 50 amp house breaker is off AND ALL THE OTHER breakers are off. Yeah, I know it's not the right way to do it and technically illegal, but in a pinch, it will work.


Dude, just buy a simple interlock kit and be done with it

_________________________
"The evidence demands a verdict".
(Re:VOA)"it's nearly impossible to actually know the particular additives that are in there at what concentrations."

Top
#4689260 - 03/08/18 11:33 PM Re: Generator connection [Re: Donald]
WyrTwister Offline


Registered: 01/13/13
Posts: 1487
Loc: Texas
The interlock kit is a very good & simple solution .

I think someone said they have a cord coming from the generator with a male end , that plugs into the house system . Never do this , those prongs / blades will become hot when the generator is run . " Danger , Will Robinson ! "

Or , have I got that reversed ?

You must never have a situation where you energize the prongs / blades of a male cord cap , while it is not plugged into something . Not when it is dangeling around .
_________________________
Wyr
God bless