Recent Topics
Cracked single stage paint
by JHZR2. 09/18/18 01:45 PM
Options versus dealer oil changes
by Schmoe. 09/18/18 01:34 PM
Longevity of Mercon LV in a 2017 Ford Escape?
by mrdctaylor. 09/18/18 01:24 PM
I'm on a Lawn Boy jag
by andyd. 09/18/18 01:13 PM
Old (New) Tires
by ET16. 09/18/18 12:05 PM
iOs 12 for Apple
by madRiver. 09/18/18 12:01 PM
Synthetic oil overrated??
by Ablebody. 09/18/18 12:01 PM
Ferrari Monza SP 1/2
by DeepFriar. 09/18/18 11:58 AM
Any option to "Mark all forums read"
by Rick505. 09/18/18 11:54 AM
1981 280ZX Turbo
by 16HC. 09/18/18 11:12 AM
Muscle car emblems
by Snagglefoot. 09/18/18 10:15 AM
Burn out question
by Fitter30. 09/18/18 10:15 AM
Collector Oil Cans
by Snagglefoot. 09/18/18 10:06 AM
Thoughts on this truck and price.
by ls1mike. 09/18/18 08:39 AM
Canadian Tire Lucas Synthetic Motorcycle Oil 20w50
by Snagglefoot. 09/18/18 07:58 AM
Blast from my past
by 53' Stude. 09/18/18 07:25 AM
Happy Birthday USAF!
by Astro14. 09/18/18 06:35 AM
Ever had a total engine failure?
by Exhaustgases. 09/18/18 02:58 AM
Newest Members
tomkat22, tabar2004, SierraMan, Rennmeister, KeithCoates
66004 Registered Users
Who's Online Now
105 registered members (Analyzer, 2010Civic, AndyB, 2009Edge, Ablebody, andyd, 14 invisible), 1,792 guests, and 42 spiders.
Key: Admin, Global Mod, Mod
Forum Statistics
Forums67
Topics290,597
Posts4,847,119
Members66,004
Most Online3,590
Jan 24th, 2017
Donate to BITOG
Previous Thread
Next Thread
Print Thread
Hop To
Generator connection #4687781
03/07/18 05:37 PM
03/07/18 05:37 PM
Joined: Mar 2004
Posts: 20,743
Upstate NY
Donald Offline OP
Donald  Offline OP
Joined: Mar 2004
Posts: 20,743
Upstate NY
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.

Last edited by Donald; 03/07/18 05:39 PM.

2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2016 Subaru Crosstrek CVT (wife's)
Re: Generator connection [Re: Donald] #4687806
03/07/18 06:02 PM
03/07/18 06:02 PM
Joined: Jan 2013
Posts: 1,833
Texas
WyrTwister Offline
WyrTwister  Offline
Joined: Jan 2013
Posts: 1,833
Texas
I would change " gender " of the outlet .

Be 100% certain you do not end up with a system where the blades on the male do not end up " hot " when the generator is running .

If they are exposed & flopping around , some one may easily get " bit " .


Wyr
God bless
Re: Generator connection [Re: Donald] #4687819
03/07/18 06:14 PM
03/07/18 06:14 PM
Joined: Mar 2004
Posts: 20,743
Upstate NY
Donald Offline OP
Donald  Offline OP
Joined: Mar 2004
Posts: 20,743
Upstate NY
The outlet has a snap cover so if a connector is not inserted the outlet will be covered.


2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2016 Subaru Crosstrek CVT (wife's)
Re: Generator connection [Re: Donald] #4687836
03/07/18 06:23 PM
03/07/18 06:23 PM
Joined: Jan 2009
Posts: 282
San Diego, California
Jim_Truett Offline
Jim_Truett  Offline
Joined: Jan 2009
Posts: 282
San Diego, California
Sounds like the box has an Inlet, not an Outlet. You will need to change it to be safe and legal.


2008 F250 6.4 PowerStroke 43k
2005 Honda CR-V 193k
2005 Honda Pilot 235k
1963 Nova SS 84k
2015 Civic Si 23k
2013 Mahindra 3016HST 99hrs
Re: Generator connection [Re: Donald] #4687894
03/07/18 07:11 PM
03/07/18 07:11 PM
Joined: Dec 2016
Posts: 6,226
Waco, TX
Linctex Offline
Linctex  Offline
Joined: Dec 2016
Posts: 6,226
Waco, TX
What are your plans for said generator?

Emergency stand-by, or......?


"The evidence demands a verdict".
(Re:VOA)"it's nearly impossible to actually know the particular additives that are in there at what concentrations."
Re: Generator connection [Re: Donald] #4687943
03/07/18 07:55 PM
03/07/18 07:55 PM
Joined: Mar 2004
Posts: 20,743
Upstate NY
Donald Offline OP
Donald  Offline OP
Joined: Mar 2004
Posts: 20,743
Upstate NY
It will be a backup and will power parts of my home via a generator cord.


2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2016 Subaru Crosstrek CVT (wife's)
Re: Generator connection [Re: Donald] #4687986
03/07/18 08:24 PM
03/07/18 08:24 PM
Joined: Dec 2017
Posts: 2,301
SE British Columbia, Canada
Snagglefoot Offline
Snagglefoot  Offline
Joined: Dec 2017
Posts: 2,301
SE British Columbia, Canada
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.


Sounds like someone wired it so they could run a conventional cord to your generator. Youíre supposed to use a special generator cord. They wired it like an RV trailer but didnít realize itís against code because a house can be powered from the grid but the RV would not.


If you want the job done right......do it yourself.
Re: Generator connection [Re: Donald] #4688066
03/07/18 09:32 PM
03/07/18 09:32 PM
Joined: Dec 2017
Posts: 2,301
SE British Columbia, Canada
Snagglefoot Offline
Snagglefoot  Offline
Joined: Dec 2017
Posts: 2,301
SE British Columbia, Canada
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.
Originally Posted By: Donald
I have a power box to bolt on to my generator to provide power. It's got a double 30 amp breaker and a 4 wire twist lock outlet. The problem is the outlet is male and it should be female of course. Do I try and find a round L14-30 female outlet that will fit or make a short female to female cord.


Checked it out and assuming your inlet was wired correctly, you have the correct configuration. . My comments above are incorrect. The inlet to the house will be a male plug. This will allow a heavy gauge cord to be plugged into the female plug on the generator and the female end of the generator cord will plug into the house. Inside will be a switch that will isolate the grid from the house and allow the inlet to the house to connect to the house wiring. When wired correctly there is no way for grid power to energize the male plug. Also when done correctly your house breakers willl still be functional. Hope that helps.


If you want the job done right......do it yourself.
Re: Generator connection [Re: Donald] #4688517
03/08/18 10:29 AM
03/08/18 10:29 AM
Joined: May 2003
Posts: 7,321
Oklahoma
Schmoe Online content
Schmoe  Online Content
Joined: May 2003
Posts: 7,321
Oklahoma
That's what I've done, but the opposite. Installed a 50 amp breaker and a dedicated female plug in the garage. Output from the generator to a 50 amp rated cord connected to a male plug that goes into that house female plug. First, turn off the main breaker so there is no back feed. Hook up all the cables and make sure 50 amp house breaker is off AND ALL THE OTHER breakers are off. Fire up generator and let warm up. Turn on breakers from the generator, turn on dedicated 50 amp house breaker, then slowly turn on the home breakers that I need. You'll have to label all your breakers for the house because some of them you won't need to use and save power for the generator. I keep the kitchen one on, stove is a 40 amp breaker and it stays off, living room, bathroom, one bedroom and the floor freezers if it is in summer time, but those things stay insulated for a pretty long time. Yeah, I know it's not the right way to do it and technically illegal, but in a pinch, it will work.


01 Supercrew Lariat 4X4
06 Accord EX-L V6
14 CRV EX-L
Re: Generator connection [Re: Donald] #4688556
03/08/18 11:09 AM
03/08/18 11:09 AM
Joined: Dec 2017
Posts: 2,301
SE British Columbia, Canada
Snagglefoot Offline
Snagglefoot  Offline
Joined: Dec 2017
Posts: 2,301
SE British Columbia, Canada
The problem with technically illegal is that you technically have no house insurance. Just install the proper isolation switch and breaker. If someone throws the main breaker you can electrocute a lineman.


If you want the job done right......do it yourself.
Re: Generator connection [Re: Donald] #4688698
03/08/18 01:33 PM
03/08/18 01:33 PM
Joined: May 2007
Posts: 7,507
Indianapolis, IN
dnewton3 Offline
dnewton3  Offline
Joined: May 2007
Posts: 7,507
Indianapolis, IN
I have built my last two homes myself (acted as GC and did a lot of the work myself).

When I wired my homes, I put in a few secondary circuits to the major items (furnace, fridge, septic pump, tv, etc).
Each outlet has a twin circuit; one side for Duke energy and one for the Generator. (if you break the little tab between the sockets, they become independent outlets).

All I have to do is power my secondary distribution box, then pull the appliance cord from the Duke side and into the Gen side. Viola!

And no risk whatsoever of killing a worker upstream by powering the main line into a hot condition.


The act of preventative maintenance, in and of itself, is FAR MORE important than brand/grade/base choices among lubes and filters.
- under maintaining something is akin to abuse/neglect; that can kill equipment by shortening the lifespan
- over maintaining something has never been proven to be anything but a waste of time and money
Re: Generator connection [Re: Donald] #4688705
03/08/18 01:41 PM
03/08/18 01:41 PM
Joined: Jan 2013
Posts: 1,833
Texas
WyrTwister Offline
WyrTwister  Offline
Joined: Jan 2013
Posts: 1,833
Texas
There are many was of doing it wrong which work either most of the time or all the time . But still , they are unsafe .


Wyr
God bless
Re: Generator connection [Re: Donald] #4688732
03/08/18 02:12 PM
03/08/18 02:12 PM
Joined: Dec 2002
Posts: 4,146
The Garden State
Whimsey Offline
Whimsey  Offline
Joined: Dec 2002
Posts: 4,146
The Garden State
When I bought my 5500 watt B&S portable generator I also got a Reliance manual transfer switch. Mine's a 6 circuit switch. It's set up to not be able to back feed from the generator to the circuit breaker panel. It's either only off, line or generator so it can't back feed. It has a male 30 amp receptacle to plug the female end of the 30 amp cord plugged into the generator.

Whimsey

Re: Generator connection [Re: Schmoe] #4689201
03/08/18 10:41 PM
03/08/18 10:41 PM
Joined: Dec 2016
Posts: 6,226
Waco, TX
Linctex Offline
Linctex  Offline
Joined: Dec 2016
Posts: 6,226
Waco, TX
Originally Posted By: Schmoe
That's what I've done, but the opposite. Installed a 50 amp breaker and a dedicated female plug in the garage. Output from the generator to a 50 amp rated cord connected to a male plug that goes into that house female plug. First, turn off the main breaker so there is no back feed. Hook up all the cables and make sure 50 amp house breaker is off AND ALL THE OTHER breakers are off. Yeah, I know it's not the right way to do it and technically illegal, but in a pinch, it will work.


Dude, just buy a simple interlock kit and be done with it



"The evidence demands a verdict".
(Re:VOA)"it's nearly impossible to actually know the particular additives that are in there at what concentrations."
Re: Generator connection [Re: Donald] #4689260
03/09/18 12:33 AM
03/09/18 12:33 AM
Joined: Jan 2013
Posts: 1,833
Texas
WyrTwister Offline
WyrTwister  Offline
Joined: Jan 2013
Posts: 1,833
Texas
The interlock kit is a very good & simple solution .

I think someone said they have a cord coming from the generator with a male end , that plugs into the house system . Never do this , those prongs / blades will become hot when the generator is run . " Danger , Will Robinson ! "

Or , have I got that reversed ?

You must never have a situation where you energize the prongs / blades of a male cord cap , while it is not plugged into something . Not when it is dangeling around .


Wyr
God bless