Recent Topics
Ford WSS-M2C937-A > Ford WSS-M2C946-A ?
by 89Rustang
29 minutes 53 seconds ago
Save $8.62 at Amazon today...
by 2dogs
Today at 12:22 PM
proud dad!
by RichardS
Today at 12:04 PM
GMs Opel subsidiary to be sold to the French
by chrisri
Today at 11:59 AM
UPS battery maintenance?
by Quattro Pete
Today at 11:47 AM
No spark B&S Intek 205cc
by Oldmoparguy1
Today at 09:33 AM
Oil filter for 2003 Chevy Tahoe
by jxthomps
Today at 09:03 AM
Very Infrequently Used Truck / Maintenance
by Miller88
Today at 07:32 AM
Honda K24 Tapping / Cam galling - what to quiet it
by 91e30181
Today at 07:15 AM
Germany and renewable energy
by wemay
Today at 06:12 AM
International news - India
by Rick in PA
Today at 03:27 AM
Penrite 5W-20 & 15W-60 in Oz
by SR5
Today at 01:57 AM
YOUR eds red?
by buck91
Yesterday at 11:53 PM
K&n open element
by buck91
Yesterday at 11:49 PM
Wilson branded alternators? any good?
by Mr_Accord
Yesterday at 10:59 PM
2013 Civic low speed hesitation
by Dohc98vteC
Yesterday at 10:36 PM
Letís discuss high mileage modern engine life...
by Owenslee
Yesterday at 09:40 PM
Sunoco about to join the Top Tier List
by Tdbo
Yesterday at 09:34 PM
Blower + mods require higher end oil?
by c5z06
Yesterday at 09:01 PM
F-250 Ball Joint Replacement
by mobilaltima
Yesterday at 08:34 PM
Newest Members
EvelynJane, anwar5557, mitsu4me, Samrsnow, Ozlander
60607 Registered Users
Who's Online
88 registered (aquariuscsm, 89Rustang, 2015_PSD, 2dogs, 69GTX, 8 invisible), 2141 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
60607 Members
66 Forums
261410 Topics
4312244 Posts

Max Online: 3590 @ 01/24/17 08:07 PM
Donate to BITOG
Topic Options
#3372743 - 05/15/14 06:20 PM Furnace Condensate Line Clogged
JerryBob Offline


Registered: 04/11/13
Posts: 921
Loc: Colorado
Does anyone know how and where to unclog a condensate line on a Carrier furnace (circa 2010)? The unit has started creating puddles since I've turned on the AC.

The photo below shows where I think it is, but I am not sure. Does the black corrugated tube on the left that goes into the white housing (the area with all the tags hanging off of them) need to come off and flushed out somehow?

I think the leak is coming from the white PVC drain on the extreme lower right. I made sure that the piece going to the floor drain is not clogged, so I think the clog is somewhere within the unit.

Any advice to save a service call would be greatly appreciated.



_________________________
Certified Filter Cutter - License #F-23567 Expires 12/2019

Top
#3372762 - 05/15/14 06:54 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
Corvette Owner Offline


Registered: 01/22/03
Posts: 1676
Loc: Waldorf, Maryland
Can you use air pressure with a rag (to seal one end) to blow out line? That's how I clear mine.


Edited by Corvette Owner (05/15/14 07:08 PM)
_________________________
Vehicles:
98 Corvette
06 Murano
96 Chevy Van (Custom Conversion)
14 Chevy Impala
10 Starcraft Boat
13 Buick Enclave

Top
#3372768 - 05/15/14 07:18 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
laserred96gt Offline


Registered: 03/03/13
Posts: 760
Loc: Florida
What I see in the pics is your gas line, PVC drain pipe connects to your evaporator coil which is probably on top of you furnace. There should be a service port ( where you can pour vinegar to help keep the drain clean, if they even installed one ) you can try to gently blow it out, or go outside find where the drain comes out and try to vacuum it. Im surprised the float switch hasn't tripped, or if it even has one.


Edited by laserred96gt (05/15/14 07:22 PM)
_________________________
96 Mustang GT: Maxlife 5W30
04 E-150, 4.6, 208K, PP 5W20
11 Camry 2.5, 46K, Castrol Edge 0W20.

Top
#3372773 - 05/15/14 07:30 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
bepperb Offline


Registered: 01/10/08
Posts: 4966
Loc: Milwaukee, WI
Those black tubes are for condensate from the heat exchanger. Look for something above the furnace itself. Also, I see the pvc pipe. Don't be afraid to remove the panel below the one you've removed (with the little window to view the diagnostic led), though it will have a switch and the furnace won't run with that one removed.
_________________________
2004 Highlander 2.4
2011 Toyota Sienna 3.5
Recently Gone:
2006 Accord 2.4l K24A8
1993 Kawi EX 500

Top
#3372777 - 05/15/14 07:37 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
JC1 Offline


Registered: 11/29/08
Posts: 2022
Loc: Oshawa, Ontario Canada
Originally Posted By: JerryBob
Does anyone know how and where to unclog a condensate line on a Carrier furnace (circa 2010)? The unit has started creating puddles since I've turned on the AC.

The photo below shows where I think it is, but I am not sure. Does the black corrugated tube on the left that goes into the white housing (the area with all the tags hanging off of them) need to come off and flushed out somehow?

I think the leak is coming from the white PVC drain on the extreme lower right. I made sure that the piece going to the floor drain is not clogged, so I think the clog is somewhere within the unit.

Any advice to save a service call would be greatly appreciated.



Jerrybob,

Your condensate trap is that white box with the two black hoses in it. It gets all gunked up with crud. You'll need to remove the lower door to get it out. There are two tabs that you squeeze on each side and pull the trap up. You can rinse it out with water from a tap or soak it in vinegar for a while.

Here is a link to the part.
http://www.repairclinic.com/PartDetail/Drain-Pan/319830402/2347566

I had a similar furnace. Just replaced it last December due to the heat exchangers rusting out.

Regards, JC.
_________________________
2015 Grand Caravan SXT Plus 5w-20 PPPP/Wix Filter
1997 Honda Civic CX 5w-30 Mobil 1/Napa Gold Filter

Top
#3372779 - 05/15/14 07:37 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
marshall25 Offline


Registered: 07/10/04
Posts: 84
Loc: Indiana
If it's from the AC, your condensate pan on the coil is probably blocked, then over flowing and draining out through the furnace. Pull the cover off your A-coil and check it out.

Top
#3372802 - 05/15/14 08:14 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
Chris Meutsch Offline


Registered: 02/27/06
Posts: 2499
Loc: Cincinnati
My service tech pours bleach down the drain pipe coming straight from the A-coil every year and tells me to do it every 3 months to keep things clean. I never do, but never had a problem. I second what others have said, it's the coil pan drain.
_________________________
"I've never heard 'Taco Bell' and 'tasty' mentioned in the same sentence before."
---mclasser, 7/25/16

Top
#3372847 - 05/15/14 09:16 PM Re: Furnace Condensate Line Clogged [Re: Chris Meutsch]
DSparks Offline


Registered: 12/19/13
Posts: 495
Loc: San Antonio, Texas
Pvc fittings at very bottom left of the pic is the drain .....the evaporator sits in a pan and the water runs out of this drain to the outside...basically its plugged up with slime and crud.....2 ways to clean it...quick way is to blow air from outside and should clear it but will probably be temporary but will buy you some time...or take the lower panels and fittings apart and maybe remove coil and pan completely to clean it all real good....just depends how bad it is...

Top
#3373308 - 05/16/14 01:34 PM Re: Furnace Condensate Line Clogged [Re: JerryBob]
ironman_gq Offline


Registered: 04/30/14
Posts: 515
Loc: MN
Our HVAC tech uses compressed air to blow out the lines and clear the clogs, he then follows up by pouring bleach down the lines to kill the mold and crud that eventually clogs the lines.