Yeah, 1000 watts...A little over 8 amps. According to
Engineering Toolbox, 1/3HP motor on 115VAC is gonna pull over 7 amps. 1/2HP is gonna need almost 10 amps. Some motors are more efficient than others, but that should ballpark it. So if his sump pump is anything more than 1/3HP it won't run it.
And that is only talking of steady state. Motor start current can be up to nearly an order of magnitude greater. Most inverters/generators rated to run induction motors have a massive short term surge rating to get the motor started. Those that don't either pop a breaker, stall or drop the output voltage way past the point of usefulness and eventually either smoke the generator or motor.
I've had a 2500W generator that would not start a 1000W compressor but would drive a 2500W fan heater all day long. Measured estimates for start current were in the order of 5 x steady state running current on that device, and that was only a little one.
Originally Posted By: Joshua_Skinner
Rotating machinery usually has a fair wave form, but who know about that little genny. That the OP tried using such a generator to run a sump pump says a lot about his knowledge level.
Agreed, but it does not take much of a wave form error for the non-RMS meters to give wacky readings, and inductive machines don't tend to give nice sinusoidal waveforms into an open circuit. You get all sorts of peculiar distortions. Put a 20W light bulb on it and it'll settle down and look much more reasonable.