Originally Posted By: jrustles
That is true, but since these are simple resistive loads, they will simply draw less current with less voltage, thus less work (output) and the current derating on 208v. if this were another type of (non-resistive) load that required a certain amount of work output, then yes it would draw more amps with lower voltage to equal the same work.
V=I*R
Thus for a given resistance, voltage and current have to directly scale.
Just for simplicity, in a 1 ohm load, 240V would yield 240A, while in that same load, 208V would only take 208A. Voltage is a driving force in that variant of the equation, such that the higher potential,the more current you can flow across that resistor in theory.
For the OP, chances are practically you'll be fine if you're not talking continuous use/duty, and particularly if you preheat one oven first then the other. Often the breaker ratings are based upon adding up all loads operating fully at once.
Still, breakers can only handle some fraction of full rating (there are usually curves for this, they have to allow some amount over their rating for some time to allow for inrush currents, but the balance is that vs opening too slow in other cases), as can wire so a high enough insulation temperature rating. Doesn't mean I'd chance it at all under any circumstance. Let's say there is an electrical fire, or any fire in the kitchen, and the house isn't a total loss (parts can be studied), I'm sure it would be sop to look at wiring and breakers. I wouldn't want to take that chance. No doubt things get under wired or done poorly to save cost... And you're right on the cusp... But I'd not chance it...
That is true, but since these are simple resistive loads, they will simply draw less current with less voltage, thus less work (output) and the current derating on 208v. if this were another type of (non-resistive) load that required a certain amount of work output, then yes it would draw more amps with lower voltage to equal the same work.
V=I*R
Thus for a given resistance, voltage and current have to directly scale.
Just for simplicity, in a 1 ohm load, 240V would yield 240A, while in that same load, 208V would only take 208A. Voltage is a driving force in that variant of the equation, such that the higher potential,the more current you can flow across that resistor in theory.
For the OP, chances are practically you'll be fine if you're not talking continuous use/duty, and particularly if you preheat one oven first then the other. Often the breaker ratings are based upon adding up all loads operating fully at once.
Still, breakers can only handle some fraction of full rating (there are usually curves for this, they have to allow some amount over their rating for some time to allow for inrush currents, but the balance is that vs opening too slow in other cases), as can wire so a high enough insulation temperature rating. Doesn't mean I'd chance it at all under any circumstance. Let's say there is an electrical fire, or any fire in the kitchen, and the house isn't a total loss (parts can be studied), I'm sure it would be sop to look at wiring and breakers. I wouldn't want to take that chance. No doubt things get under wired or done poorly to save cost... And you're right on the cusp... But I'd not chance it...