Recent Topics
Boston, MA. What to do in short visit?
by 97tbird
08/21/14 11:40 AM
Ht/Hs value of valvoline vr1 10w30 conventional
by joegreen
08/21/14 09:56 AM
Oil additives
by minis
08/21/14 09:46 AM
Toro Suzuki 4cycle Recycler
by Ope_Freak
08/21/14 08:36 AM
Steel vs. Alloy for Winter Use?
by kkreit01
08/21/14 08:34 AM
amsoil ATM 10w30 virgin sample result
by pb
08/21/14 07:51 AM
BITOG Site Problems Help
by Smoky14
08/21/14 07:19 AM
ripped strut boots, 08 matrix.
by JustinH
08/21/14 07:04 AM
Discount Tire Direct Labor Day Sale
by sopususer
08/21/14 05:08 AM
Fixed another annoying Chevy noise
by Realtech214
08/21/14 03:51 AM
DI intake valves CAN be cleaned with PEA?
by Alext
08/21/14 01:27 AM
Longer Oil Filter,Yes I Need One
by rrounds
08/21/14 12:44 AM
Newest Members
plumcrazy, davidperrysmith, FilterMinder1, hammms, 73bug
51030 Registered Users
Who's Online
99 registered (05LGTLtd, 4wheeldog, 3800Series, 123Saab, ag_ghost, 97tbird, 10 invisible), 1990 Guests and 213 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
51030 Members
64 Forums
218095 Topics
3437834 Posts

Max Online: 2862 @ 07/07/14 03:10 PM
Donate to BITOG

Topic Options
#1858983 - 04/15/10 07:39 PM Industrial generator with 1 hour on it..
dirtymudder Offline


Registered: 10/28/02
Posts: 45
Loc: michigan
In the past year. The generator is inside of a heated building and has a block heater on it 24/7. I know it should have been run on load over the past year but that is past history. question is would you change the oil even though it has only one hour on it? By the way when it runs it supply's 480 volt to a 100hp motor.

Top
#1858993 - 04/15/10 07:50 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
Steve S Offline


Registered: 01/20/03
Posts: 18449
Loc: East of IGO
A used oil analysis costs around $30.00 to have done and would tell how the oils condition. What does the manufacture recommend?
_________________________
Why do people post I want the best for my car,,, When there isn't anything that is the best on the car to begin with.

Top
#1859038 - 04/15/10 08:38 PM Re: Industrial generator with 1 hour on it.. [Re: Steve S]
MolaKule Offline


Registered: 06/05/02
Posts: 14312
Loc: Midwest
Is it using any oil and has it been run-in?

I assume it's a diesel with about a 100kW output?
_________________________
Don't confuse my personality with my attitude. My personality is who I am. My attitude is who you are. smile

Top
#1859084 - 04/15/10 09:30 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
bruce381 Offline


Registered: 06/23/05
Posts: 3324
Loc: Millbrae, CA
Originally Posted By: dirtymudder
In the past year. The generator is inside of a heated building and has a block heater on it 24/7. I know it should have been run on load over the past year but that is past history. question is would you change the oil even though it has only one hour on it? By the way when it runs it supply's 480 volt to a 100hp motor.



no

Top
#1860482 - 04/17/10 12:20 AM Re: Industrial generator with 1 hour on it.. [Re: bruce381]
D-Roc Offline


Registered: 11/23/05
Posts: 1525
Loc: CFB Petawawa, Ontario
Plugged in 24/7...I'd be more inclined to test the coolant.
_________________________
"Close your eyes
Look deep in your soul
Step outside yourself
And let your mind go"

Top
#1865021 - 04/20/10 06:24 PM Re: Industrial generator with 1 hour on it.. [Re: D-Roc]
dirtymudder Offline


Registered: 10/28/02
Posts: 45
Loc: michigan
Generator has about 2200 hours on it.

Top
#1947404 - 07/09/10 05:56 AM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
NesloOne Offline


Registered: 07/06/10
Posts: 7
Loc: Denmark
I feel you do the test, although it will say the oil is still in good condition.
_________________________
dieselfuel, hydraulicoil, coalmine

Top
#3222658 - 12/20/13 12:34 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
JR Offline


Registered: 08/08/04
Posts: 920
Loc: Michigan born but my heart bel...
If it only has 1hr on the current fill a uoa will say keep in service. i wouldn't change or sample the oil. it has no use on it.
i would be more concerned about not running it time to time. if it were mine i would run it up to temp under load every 3 to 6 months.

ken

Top
#3223292 - 12/21/13 12:55 AM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
Fraser434 Offline


Registered: 09/17/11
Posts: 56
Loc: Chicago
Old Thread, i'm in power generation field service, I see this on a daily basis. Nothing wrong with taking fluid samples and inspecting the generator and transfer switch(s) for proper operation.

CAT put out the option to offer 3 year oil change cycle on CAT diesels C9 and larger in Standby Power application. Can do this by taking quarterly samples and annual filter replacement, still maintain CAT warranty or ESC.

I can tell you a very large telecom company mandates oil changes are to be performed every 3 years or per sample analysis on standby generators.

Still you have issues with engines sitting, injector cups leaking coolant, oil cooler leaking, head gasket or fuel dilution. Just changing the engine oil won't correct these issues and only mask them over for a short period.

Hope this helps.



Edited by Fraser434 (12/21/13 12:59 AM)