Recent Topics
GM 55560202 longlife cut open - 10782km
by turboseize
Today at 04:54 AM
Coolant Question.
by Farmer
Today at 04:20 AM
Stocking up for the Eco
by buck91
Today at 12:25 AM
Mobil 1 10w40 HM
by SubyRoo
Today at 12:16 AM
What type of glue for door panels?
by Nick1994
Today at 12:07 AM
Painting rear of chrome bumpers
by buck91
Yesterday at 11:09 PM
Walmart Rifle Clearance
by hatt
Yesterday at 10:44 PM
Vehicles That Must Idle For Long Periods Of Time
by BlueOvalFitter
Yesterday at 10:30 PM
2013 Taurus SHO Ecoboost
by SHO
Yesterday at 10:11 PM
Need recommendation
by double vanos
Yesterday at 10:00 PM
Kawasaki must be completely full of gas to start
by jrcowboys
Yesterday at 09:36 PM
Un-Screwing
by Ducked
Yesterday at 09:05 PM
Newest Members
therhett17, glldprimr, krankshaft, Tony_Rhed, greasemonkey1
58935 Registered Users
Who's Online
41 registered (97f150, Bandito440, b1amgm47, BobFout, bmod305, BigTrees, 2 invisible), 892 Guests and 39 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
58935 Members
66 Forums
253610 Topics
4163228 Posts

Max Online: 2862 @ 07/07/14 03:10 PM
Donate to BITOG
Topic Options
#3133836 - 09/23/13 08:03 PM Wall Power Outlet upside down...
mattwithcats Offline


Registered: 06/13/13
Posts: 1351
Loc: Virginia
I made an error today while fixing the garbage disposal.
I replaced the fried wall outlet that was the cause of the problem, wired it correctly, but installed it upside down...

Will this matter?

Used a GFCI, ugly grey, was cheaper than white or almond...
It's under the sink, so you can't see it....
_________________________
2009 Smart Pure
Pennzoil Platinum Euro 5W-40, Purolator Synthetic PSL 14610, 45 mpg...
185/55R15 General HP tires, "H" speed rated, 44 psi (300 kpa)

Top
#3133842 - 09/23/13 08:09 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Donald Offline


Registered: 03/21/04
Posts: 17176
Loc: Upstate NY
Well it almost does not matter. Is the ground at the top or bottom. Ground at the bottom is old school. Ground at the top prevents something like a paper clip or bobby pin dropped between the plug and outlet from contacting hot without popping the breaker.
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2001 Jeep Grand Cherokee Laredo 4.0- sold
1999 Dodge Ram 2500 w/Cummins- 4-sale


Top
#3133843 - 09/23/13 08:10 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Pop_Rivit Offline


Registered: 02/09/08
Posts: 5606
Loc: Midwest
It makes no difference-there's no such thing as upside down. I never met an electrical inspector that cared either way-just as long as they were wired correctly and worked.

Top
#3133846 - 09/23/13 08:12 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Jeffy_D Offline


Registered: 01/27/12
Posts: 305
Loc: missouri
As long as its wired correctly it will be fine
_________________________
10 titan 70k castrol magnatec/fram TG
12 sonic 55k AC Delco oil and filter



Top
#3133847 - 09/23/13 08:12 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
eljefino Offline


Registered: 06/15/03
Posts: 29574
Loc: ME
Hospitals seem to like having the ground on top. They're somewhat crazy.

Top
#3133867 - 09/23/13 08:30 PM Re: Wall Power Outlet upside down... [Re: Pop_Rivit]
cmorr Offline


Registered: 12/10/06
Posts: 621
Loc: Exeter Twp, PA
Originally Posted By: Pop_Rivit
It makes no difference-there's no such thing as upside down. I never met an electrical inspector that cared either way-just as long as they were wired correctly and worked.


Correct, most commercial electricians install ground plug up, residential ground side down

It is not addressed in the NEC (was raised and rejected)

18-36 Log #3897 NEC-P18 Final Action: Reject
(406.4(B))

_______________________________________________________________
Submitter: Ronald Standley, E Light Electric Services
Recommendation: Add new text as follows:
Exception No. 1: Where metal cover plates are installed, receptacles shall be
mounted such that the ground pin opening is above the hot and neutral
openings.
Substantiation: If multiple failing conditions are encountered (i.e., plug not
fully inserted, metal cover loosens, etc.) it is possible that the metal cover
could contact the hot conductor creating a short circuit and a fire hazard.
Panel Meeting Action: Reject
Panel Statement: This proposal is not substantiated with incident data
indicating burn or electrocution exposure or the circumstances surrounding
such incidents.
Additionally, the proposal only addresses receptacles installed in a vertical
plane. How does one insure in a receptacle mounted on a horizontal surface
that the ground pin opening is above the hot and neutral openings?
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
_________________________
2008 Focus Mobil 1 5W20 Napa Platinum
2006 Caravan Defy 5W20 Napa Gold
2003 PT Cruiser PYB 5W30 Pureone

Top
#3133873 - 09/23/13 08:35 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
mattwithcats Offline


Registered: 06/13/13
Posts: 1351
Loc: Virginia
Note that I used a GFCI, location is near kitchen sink..

Both bathrooms also have GFCI's...
_________________________
2009 Smart Pure
Pennzoil Platinum Euro 5W-40, Purolator Synthetic PSL 14610, 45 mpg...
185/55R15 General HP tires, "H" speed rated, 44 psi (300 kpa)

Top
#3133884 - 09/23/13 08:50 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Donald Offline


Registered: 03/21/04
Posts: 17176
Loc: Upstate NY
I have always wired disposals direct with a wall switch.
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2001 Jeep Grand Cherokee Laredo 4.0- sold
1999 Dodge Ram 2500 w/Cummins- 4-sale


Top
#3133936 - 09/23/13 09:52 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Kruse Offline


Registered: 10/05/05
Posts: 3747
Loc: Kansas
Most electricians will say that the only thing that matters is that all of them (in the same business or residence) are all installed the same, either up or down doesn't really matter, just that all of them are either up or down.

Top
#3133957 - 09/23/13 10:19 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
tom slick Offline


Registered: 05/26/03
Posts: 9006
Loc: Central Coast, Calif.
Some electricians will install a receptacle that is on a switch with the ground hole up. They can be installed sideways also.
_________________________
You get what you pay for...
So keep in mind how much you paid for this advice.

Top
#3134093 - 09/24/13 06:42 AM Re: Wall Power Outlet upside down... [Re: mattwithcats]
kb01 Offline


Registered: 10/05/09
Posts: 932
Loc: USA
Upside down receptacles and tan wire nuts seem to be the hallmark of professional electricians.

Top
#3134275 - 09/24/13 10:15 AM Re: Wall Power Outlet upside down... [Re: kb01]
Blaze Offline


Registered: 12/31/10
Posts: 1268
Loc: Washington State (East)
Originally Posted By: kb01
Upside down receptacles and tan wire nuts seem to be the hallmark of professional electricians.
yes,, mine was done that way when we had the remodel done. Had to get used to it but no problem now.

Top
#3134406 - 09/24/13 11:55 AM Re: Wall Power Outlet upside down... [Re: mattwithcats]
zzyzzx Offline


Registered: 05/18/12
Posts: 3378
Loc: Baltimore, Maryland, USA
I have the one outlet for my gas dryer upside down intentionally, since that's the way the cord seems to be wired. Presumably the manufacturer thinks I want to put it on the same outlet as my washer. Other than that, all of mine are right side up. It makes no difference if it's upside down, as long as it's wired correctly!