Recent Topics
killing weeds without poisoning well
by oilboy123
27 minutes 18 seconds ago
1999 ford expedition factory mercon v synthetic??
by merconvvv
Yesterday at 11:40 PM
Buick 3800 - "Von Voyage" oil change?
by Alex_V
Yesterday at 10:41 PM
Low oil level light on, but level not THAT low....
by gregk24
Yesterday at 10:26 PM
Is SuperLube syn multi grease universal
by NattyBoh
Yesterday at 10:05 PM
How come discount tire doesn't use jack stands?
by motor_oil_madman
Yesterday at 09:41 PM
SAFETY ?: ramps in rear and jack stands in front
by SavagePatch
Yesterday at 09:03 PM
Pennzoil ultra 5w30 back in stock at Walmart.com
by kohnen
Yesterday at 08:37 PM
Homelite weedeater not getting fuel
by Drew99GT
Yesterday at 08:26 PM
Stability issue on 2015 F250
by Donald
Yesterday at 07:25 PM
2016 Tacoma 3.5L V6 4x4
by NavyVet88
Yesterday at 07:10 PM
Question on 05 Nissan tranny w/120k
by NattyBoh
Yesterday at 06:58 PM
Newest Members
Matt_P, tpragski, 182RG, BillHuang, jwilliamson185
58578 Registered Users
Who's Online
36 registered (Chewie, austinlunsford, c502cid, bamorris2, aquariuscsm, 4 invisible), 741 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
58578 Members
66 Forums
252174 Topics
4135116 Posts

Max Online: 2862 @ 07/07/14 03:10 PM
Donate to BITOG
Topic Options
#3133836 - 09/23/13 08:03 PM Wall Power Outlet upside down...
mattwithcats Offline


Registered: 06/13/13
Posts: 1339
Loc: Virginia
I made an error today while fixing the garbage disposal.
I replaced the fried wall outlet that was the cause of the problem, wired it correctly, but installed it upside down...

Will this matter?

Used a GFCI, ugly grey, was cheaper than white or almond...
It's under the sink, so you can't see it....
_________________________
2009 Smart Pure
Pennzoil Platinum Euro 5W-40, Purolator Synthetic PSL 14610, 45 mpg...
185/55R15 General HP tires, "H" speed rated, 44 psi (300 kpa)

Top
#3133842 - 09/23/13 08:09 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Donald Offline


Registered: 03/21/04
Posts: 17037
Loc: Upstate NY
Well it almost does not matter. Is the ground at the top or bottom. Ground at the bottom is old school. Ground at the top prevents something like a paper clip or bobby pin dropped between the plug and outlet from contacting hot without popping the breaker.
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2001 Jeep Grand Cherokee Laredo 4.0- sold
1999 Dodge Ram 2500 w/Cummins- 4-sale


Top
#3133843 - 09/23/13 08:10 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Pop_Rivit Offline


Registered: 02/09/08
Posts: 5503
Loc: Midwest
It makes no difference-there's no such thing as upside down. I never met an electrical inspector that cared either way-just as long as they were wired correctly and worked.

Top
#3133846 - 09/23/13 08:12 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Jeffy_D Offline


Registered: 01/27/12
Posts: 305
Loc: missouri
As long as its wired correctly it will be fine
_________________________
10 titan 70k castrol magnatec/fram TG
12 sonic 55k AC Delco oil and filter



Top
#3133847 - 09/23/13 08:12 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
eljefino Offline


Registered: 06/15/03
Posts: 29441
Loc: ME
Hospitals seem to like having the ground on top. They're somewhat crazy.

Top
#3133867 - 09/23/13 08:30 PM Re: Wall Power Outlet upside down... [Re: Pop_Rivit]
cmorr Offline


Registered: 12/10/06
Posts: 621
Loc: Exeter Twp, PA
Originally Posted By: Pop_Rivit
It makes no difference-there's no such thing as upside down. I never met an electrical inspector that cared either way-just as long as they were wired correctly and worked.


Correct, most commercial electricians install ground plug up, residential ground side down

It is not addressed in the NEC (was raised and rejected)

18-36 Log #3897 NEC-P18 Final Action: Reject
(406.4(B))

_______________________________________________________________
Submitter: Ronald Standley, E Light Electric Services
Recommendation: Add new text as follows:
Exception No. 1: Where metal cover plates are installed, receptacles shall be
mounted such that the ground pin opening is above the hot and neutral
openings.
Substantiation: If multiple failing conditions are encountered (i.e., plug not
fully inserted, metal cover loosens, etc.) it is possible that the metal cover
could contact the hot conductor creating a short circuit and a fire hazard.
Panel Meeting Action: Reject
Panel Statement: This proposal is not substantiated with incident data
indicating burn or electrocution exposure or the circumstances surrounding
such incidents.
Additionally, the proposal only addresses receptacles installed in a vertical
plane. How does one insure in a receptacle mounted on a horizontal surface
that the ground pin opening is above the hot and neutral openings?
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
_________________________
2008 Focus Mobil 1 5W20 Napa Platinum
2006 Caravan Defy 5W20 Napa Gold
2003 PT Cruiser PYB 5W30 Pureone

Top
#3133873 - 09/23/13 08:35 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
mattwithcats Offline


Registered: 06/13/13
Posts: 1339
Loc: Virginia
Note that I used a GFCI, location is near kitchen sink..

Both bathrooms also have GFCI's...
_________________________
2009 Smart Pure
Pennzoil Platinum Euro 5W-40, Purolator Synthetic PSL 14610, 45 mpg...
185/55R15 General HP tires, "H" speed rated, 44 psi (300 kpa)

Top
#3133884 - 09/23/13 08:50 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Donald Offline


Registered: 03/21/04
Posts: 17037
Loc: Upstate NY
I have always wired disposals direct with a wall switch.
_________________________
2015 Subaru Forester 2.5 engine/CVT
2015 Ford F250 w/Powerstroke
2001 Jeep Grand Cherokee Laredo 4.0- sold
1999 Dodge Ram 2500 w/Cummins- 4-sale


Top
#3133936 - 09/23/13 09:52 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
Kruse Offline


Registered: 10/05/05
Posts: 3722
Loc: Kansas
Most electricians will say that the only thing that matters is that all of them (in the same business or residence) are all installed the same, either up or down doesn't really matter, just that all of them are either up or down.

Top
#3133957 - 09/23/13 10:19 PM Re: Wall Power Outlet upside down... [Re: mattwithcats]
tom slick Offline


Registered: 05/26/03
Posts: 8997
Loc: Central Coast, Calif.
Some electricians will install a receptacle that is on a switch with the ground hole up. They can be installed sideways also.
_________________________
You get what you pay for...
So keep in mind how much you paid for this advice.

Top
#3134093 - 09/24/13 06:42 AM Re: Wall Power Outlet upside down... [Re: mattwithcats]
kb01 Offline


Registered: 10/05/09
Posts: 932
Loc: USA
Upside down receptacles and tan wire nuts seem to be the hallmark of professional electricians.

Top
#3134275 - 09/24/13 10:15 AM Re: Wall Power Outlet upside down... [Re: kb01]
Blaze Offline


Registered: 12/31/10
Posts: 1258
Loc: Washington State (East)
Originally Posted By: kb01
Upside down receptacles and tan wire nuts seem to be the hallmark of professional electricians.
yes,, mine was done that way when we had the remodel done. Had to get used to it but no problem now.

Top
#3134406 - 09/24/13 11:55 AM Re: Wall Power Outlet upside down... [Re: mattwithcats]
zzyzzx Offline


Registered: 05/18/12
Posts: 3303
Loc: Baltimore, Maryland, USA
I have the one outlet for my gas dryer upside down intentionally, since that's the way the cord seems to be wired. Presumably the manufacturer thinks I want to put it on the same outlet as my washer. Other than that, all of mine are right side up. It makes no difference if it's upside down, as long as it's wired correctly!

Top