Recent Topics
1982 Lincoln Town Car?
by 19jacobob93
6 minutes 28 seconds ago
Engine feel sluggy going from 5w20 to 5w30 5.4L 3v
by MetalSlug
Today at 03:59 AM
Super Bowl XLIX DVD?
by gfh77665
Today at 01:38 AM
Mechanical Keyboards
by camrydriver111
Today at 12:07 AM
Manly and unmanly foods
by hotwheels
Yesterday at 11:24 PM
I think I stole a Sig P220.....
by Blue_Goose
Yesterday at 09:51 PM
Fire forming brass
by 2cool
Yesterday at 09:49 PM
LubroMoly MOS2 $6.15/bottle.
by Hollow
Yesterday at 09:42 PM
Dealer out WRONG oil brand in and likely too much
by SumpChump
Yesterday at 09:39 PM
Kmart 5 Qt Jug - $7.74
by Greg L
Yesterday at 09:35 PM
The single worst-looking food
by hotwheels
Yesterday at 09:00 PM
Amsoil SS 0w20, 23,780 miles, '08 Civic Hybrid116K
by doublej9886
Yesterday at 08:53 PM
Newest Members
glgeek, canivour, hunky, Esgar, doublej9886
52990 Registered Users
Who's Online
40 registered (BISCUT, BigCahuna, b1amgm47, 19jacobob93, BobsArmory, bigt61, 4 invisible), 637 Guests and 181 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
52990 Members
66 Forums
227352 Topics
3626244 Posts

Max Online: 2862 @ 07/07/14 03:10 PM
Donate to BITOG
Topic Options
#1858983 - 04/15/10 07:39 PM Industrial generator with 1 hour on it..
dirtymudder Offline


Registered: 10/28/02
Posts: 50
Loc: michigan
In the past year. The generator is inside of a heated building and has a block heater on it 24/7. I know it should have been run on load over the past year but that is past history. question is would you change the oil even though it has only one hour on it? By the way when it runs it supply's 480 volt to a 100hp motor.

Top
#1858993 - 04/15/10 07:50 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
Steve S Offline


Registered: 01/20/03
Posts: 18449
Loc: East of IGO
A used oil analysis costs around $30.00 to have done and would tell how the oils condition. What does the manufacture recommend?
_________________________
Why do people post I want the best for my car,,, When there isn't anything that is the best on the car to begin with.

Top
#1859038 - 04/15/10 08:38 PM Re: Industrial generator with 1 hour on it.. [Re: Steve S]
MolaKule Offline


Registered: 06/05/02
Posts: 15047
Loc: Iowegia
Is it using any oil and has it been run-in?

I assume it's a diesel with about a 100kW output?
_________________________
Common sense and logic is a flower that does not grow in everyone's garden. smile

Top
#1859084 - 04/15/10 09:30 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
bruce381 Offline


Registered: 06/23/05
Posts: 3324
Loc: Millbrae, CA
Originally Posted By: dirtymudder
In the past year. The generator is inside of a heated building and has a block heater on it 24/7. I know it should have been run on load over the past year but that is past history. question is would you change the oil even though it has only one hour on it? By the way when it runs it supply's 480 volt to a 100hp motor.



no

Top
#1860482 - 04/17/10 12:20 AM Re: Industrial generator with 1 hour on it.. [Re: bruce381]
D-Roc Offline


Registered: 11/23/05
Posts: 1525
Loc: CFB Petawawa, Ontario
Plugged in 24/7...I'd be more inclined to test the coolant.
_________________________
"Close your eyes
Look deep in your soul
Step outside yourself
And let your mind go"

Top
#1865021 - 04/20/10 06:24 PM Re: Industrial generator with 1 hour on it.. [Re: D-Roc]
dirtymudder Offline


Registered: 10/28/02
Posts: 50
Loc: michigan
Generator has about 2200 hours on it.

Top
#1947404 - 07/09/10 05:56 AM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
NesloOne Offline


Registered: 07/06/10
Posts: 7
Loc: Denmark
I feel you do the test, although it will say the oil is still in good condition.
_________________________
dieselfuel, hydraulicoil, coalmine

Top
#3222658 - 12/20/13 12:34 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
JR Offline


Registered: 08/08/04
Posts: 932
Loc: Michigan born but my heart bel...
If it only has 1hr on the current fill a uoa will say keep in service. i wouldn't change or sample the oil. it has no use on it.
i would be more concerned about not running it time to time. if it were mine i would run it up to temp under load every 3 to 6 months.

ken

Top
#3223292 - 12/21/13 12:55 AM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
Fraser434 Offline


Registered: 09/17/11
Posts: 79
Loc: Chicago
Old Thread, i'm in power generation field service, I see this on a daily basis. Nothing wrong with taking fluid samples and inspecting the generator and transfer switch(s) for proper operation.

CAT put out the option to offer 3 year oil change cycle on CAT diesels C9 and larger in Standby Power application. Can do this by taking quarterly samples and annual filter replacement, still maintain CAT warranty or ESC.

I can tell you a very large telecom company mandates oil changes are to be performed every 3 years or per sample analysis on standby generators.

Still you have issues with engines sitting, injector cups leaking coolant, oil cooler leaking, head gasket or fuel dilution. Just changing the engine oil won't correct these issues and only mask them over for a short period.

Hope this helps.