Recent Topics
prime guard jobber cut. impressive
by Bigdaddyeasy
08/03/15 04:39 PM
Oil Filter Wrench for Acura MDX
by kjbock
08/03/15 03:39 PM
Good spot to buy PCMO's online
by HLongfoot79
08/03/15 02:39 PM
Mustang power steering fluid
by buck91
08/03/15 02:32 PM
did a oops changing oil
by chiefsfan1
08/03/15 02:14 PM
best tool for stuck oil filters??
by columnshift
08/03/15 01:18 PM
My car just got totaled for the 2nd time!
by Drew99GT
08/03/15 01:17 PM
The Reality of Self-Driving Cars
by edhackett
08/03/15 01:04 PM
2010 Subaru OB 3.6R, Chevron Supreme 5w30 again
by charger
08/03/15 12:56 PM
unsticking frozen brake drum! (87 Caravan)
by columnshift
08/03/15 12:50 PM
suburban running boards
by bmwjohn
08/03/15 12:35 PM
Pep Boys Pennzoil Platinum + Oil Filter $22.99
by Leonardo629
08/03/15 11:52 AM
Newest Members
VinceHimself, jirfyu, Donskjr, mccantsjr, kocoman
54913 Registered Users
Who's Online
82 registered (4Kings, Al, 97tbird, 901Memphis, 2civics, 2010_FX4, 8 invisible), 1920 Guests and 72 Spiders online.
Key: Admin, Global Mod, Mod
Forum Stats
54913 Members
66 Forums
235346 Topics
3786558 Posts

Max Online: 2862 @ 07/07/14 03:10 PM
Donate to BITOG
Topic Options
#1858983 - 04/15/10 07:39 PM Industrial generator with 1 hour on it..
dirtymudder Offline


Registered: 10/28/02
Posts: 52
Loc: michigan
In the past year. The generator is inside of a heated building and has a block heater on it 24/7. I know it should have been run on load over the past year but that is past history. question is would you change the oil even though it has only one hour on it? By the way when it runs it supply's 480 volt to a 100hp motor.

Top
#1858993 - 04/15/10 07:50 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
Steve S Offline


Registered: 01/20/03
Posts: 18449
Loc: East of IGO
A used oil analysis costs around $30.00 to have done and would tell how the oils condition. What does the manufacture recommend?
_________________________
Why do people post I want the best for my car,,, When there isn't anything that is the best on the car to begin with.

Top
#1859038 - 04/15/10 08:38 PM Re: Industrial generator with 1 hour on it.. [Re: Steve S]
MolaKule Offline


Registered: 06/05/02
Posts: 15706
Loc: Iowegia - USA
Is it using any oil and has it been run-in?

I assume it's a diesel with about a 100kW output?
_________________________
HORSE: You can lead a human to knowledge, but you can't make him think critically! smile

Top
#1859084 - 04/15/10 09:30 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
bruce381 Offline


Registered: 06/23/05
Posts: 3327
Loc: Millbrae, CA
Originally Posted By: dirtymudder
In the past year. The generator is inside of a heated building and has a block heater on it 24/7. I know it should have been run on load over the past year but that is past history. question is would you change the oil even though it has only one hour on it? By the way when it runs it supply's 480 volt to a 100hp motor.



no

Top
#1860482 - 04/17/10 12:20 AM Re: Industrial generator with 1 hour on it.. [Re: bruce381]
D-Roc Offline


Registered: 11/23/05
Posts: 1525
Loc: quelque part
Plugged in 24/7...I'd be more inclined to test the coolant.

Top
#1865021 - 04/20/10 06:24 PM Re: Industrial generator with 1 hour on it.. [Re: D-Roc]
dirtymudder Offline


Registered: 10/28/02
Posts: 52
Loc: michigan
Generator has about 2200 hours on it.

Top
#1947404 - 07/09/10 05:56 AM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
NesloOne Offline


Registered: 07/06/10
Posts: 7
Loc: Denmark
I feel you do the test, although it will say the oil is still in good condition.
_________________________
dieselfuel, hydraulicoil, coalmine

Top
#3222658 - 12/20/13 12:34 PM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
JR Offline


Registered: 08/08/04
Posts: 987
Loc: Michigan born but my heart bel...
If it only has 1hr on the current fill a uoa will say keep in service. i wouldn't change or sample the oil. it has no use on it.
i would be more concerned about not running it time to time. if it were mine i would run it up to temp under load every 3 to 6 months.

ken

Top
#3223292 - 12/21/13 12:55 AM Re: Industrial generator with 1 hour on it.. [Re: dirtymudder]
Fraser434 Offline


Registered: 09/17/11
Posts: 126
Loc: Chicago
Old Thread, i'm in power generation field service, I see this on a daily basis. Nothing wrong with taking fluid samples and inspecting the generator and transfer switch(s) for proper operation.

CAT put out the option to offer 3 year oil change cycle on CAT diesels C9 and larger in Standby Power application. Can do this by taking quarterly samples and annual filter replacement, still maintain CAT warranty or ESC.

I can tell you a very large telecom company mandates oil changes are to be performed every 3 years or per sample analysis on standby generators.

Still you have issues with engines sitting, injector cups leaking coolant, oil cooler leaking, head gasket or fuel dilution. Just changing the engine oil won't correct these issues and only mask them over for a short period.

Hope this helps.